non-combustible insulation???

  • dcongvt
  • dcongvt's Avatar Topic Author
  • Offline
  • New Member
  • New Member
More
12 years 8 months ago - 12 years 8 months ago #8081 by dcongvt
non-combustible insulation??? was created by dcongvt
Dear!

This extract from IMO " 9.3.7 Except for insulation in refrigerated compartments, insulation material, pipe and vent duct lagging, ceilings, linings and bulkheads should be of non-combustible material. Insulation of pipe fittings for cold service systems and vapour barriers and adhesives used in conjunction with insulation need not be non-combustible but they should be kept to a minimum and their exposed surfaces should have low flame spread characteristics28 . In spaces where penetration of oil products is possible, the surfaces of the insulation should be impervious to oil or oil vapours."

Now, I already installed insulation (which have DNV cert for Low-flame spread and satisfied IMO requirement for Low-flame spread test) for Engine Cooling Water system (working temp 100 deg C), suddenly QC came and said: why did you install it, it not non-combustible material?

I'm in big trouble now?

1. Is this really need non-combustible material?

2. IF I have to use above insulation (because of schedule and cost if take-out & re-install a new material), how can I ask the Owner for approval?

Thanks for help