Pneumatic actuator installation

  • gpsvn
  • gpsvn's Avatar Topic Author
  • Offline
  • Premium Member
  • Premium Member
More
16 years 7 months ago - 16 years 7 months ago #7188 by gpsvn
Pneumatic actuator installation was created by gpsvn
Usually, the centerline of the cylinder is parallel to the center line of the valve. One of the reasons is this configuration saves space and looks neat, nothing protruding from the pipe and blocking walkways, etc...

Is it acceptable to install the actuator with its center line perpendicular to the valve center line ? Can I rotate it 90 degree ? Appreciate the forum member opinions.

The picture below shows how it usually done.

Please Log in or Create an account to join the conversation.

More
16 years 7 months ago - 16 years 7 months ago #4218 by 11echo
Replied by 11echo on topic Actually it shouldn't make a
Actually it shouldn't make a difference in regards to the operation of the valve. The only issue I see is it would take up a larger chunk of the access area around the valve ...this may or may not be an issue, so I guess it would depend on the site. My $0.02 anyway, Good Luck! ...Mark

Please Log in or Create an account to join the conversation.

More
16 years 7 months ago - 16 years 7 months ago #4219 by Anton
Replied by Anton on topic I would echo 11echo's comments
I would echo 11echo's comments .... can be done .... but why ???

- If you're the smartest person in the room ... you're in the wrong room.

Please Log in or Create an account to join the conversation.

  • gpsvn
  • gpsvn's Avatar Topic Author
  • Offline
  • Premium Member
  • Premium Member
More
16 years 7 months ago - 16 years 7 months ago #4220 by gpsvn
Replied by gpsvn on topic Thank you both of you
Thank you both of you for the quick responses.

It's a retrofitting job. I have to convert a manual valve into an ESDV. The space I have is quite congested and installing the actuator in the usual way will cause clash. The options I have are, please feel free to add.

1. Rotate the actuator as said above.
2. Roll the valve side way or upside down
3. Shut the line down and install new ESDV at another place.

The valve locates next to an flat bend and rotating the actuator 90 degree does not take much access area if I position the spring canister on the same side of the pipe after the bend. The cylinder is sticking out a little bit but I think it's acceptable.

Please give me reasons for not doing it, apart from blocking access.

Please Log in or Create an account to join the conversation.

More
16 years 7 months ago - 16 years 7 months ago #4221 by Jop
Replied by Jop on topic As noted by others there
As noted by others there should be no reason to prevent you from rotation the operator 90 degrees to the line. Therefore you only need to seek advice from two sources.
1, The valve vendor - Do they have any objections?
2, The operators - What would they rather have?

Do it once and Do it Right

Please Log in or Create an account to join the conversation.

  • gpsvn
  • gpsvn's Avatar Topic Author
  • Offline
  • Premium Member
  • Premium Member
More
16 years 7 months ago - 16 years 7 months ago #4222 by gpsvn
Replied by gpsvn on topic This must be a record,
This must be a record, in minutes, my topic has drawn the attention of three experts on this site, including the admin.

Back to the case.

I have not checked with valve vendor, as this was purchased years ago. However, we bought some others ESDV from the same vendor, about the same time in the past, and some of them have identical valve bodies. So, I think fitting an actuator on top of the valve should not be a problem. Now, if I rotate the actuator, the forces produce by the actuator acting on the valve should be the same. If I roll the valve side way then the valve vendor will not be happy as the valve stem will have to take some loads at different direction. If I roll the valve upside down, the stem seal may get damaged overtime. That makes the valve vendor not happy. In addition, rolling the valve requires shutdown.

If I can relocate control panel so the pressure gauge is visible, the solenoid and instrument valves are accessible, I think the operator will put up little resistance.

I am working on a datasheet to procure this actuator, hoping the vendors will come back with positive responses.